Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Tuning a Temperature Process Control Loop
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > Tuning a Temperature Process Control Loop

Tuning a Temperature Process Control Loop

Last updated: February 28, 2019 12:00 pm
Editorial Staff
Control Systems
No Comments
Share
4 Min Read
SHARE

Tuning a Temperature Process Control Loop

Ziegler-Nichols open-loop tuning procedure

This next simulated process is a temperature control process. Performing an open-loop test (two 10% increasing output step-changes, both made in manual mode) on this process resulted in the following behavior:

Tuning a Temperature Process Control Loop

From the trend, the process appears to be self-regulating with a slow time constant (lag) and a substantial dead time. The reaction rate (R) on the first step-change is 30% over 30 minutes, or 1 percent per minute. Dead time (L) looks to be approximately 1.25 minutes. Following the Ziegler- Nichols recommendations for PID tuning based on these process characteristics (also including the 10% step-change magnitude Δm):

Tuning a Temperature Process Control Formula

Applying the PID values of 9.6 (gain), 2.5 minutes per repeat (integral), and 0.625 minutes (derivative) gave the following result in automatic mode:

Tuning a Temperature Process Control

As you can see, the results are quite poor. The PV is still oscillating with a peak-to-peak amplitude of almost 20% from the last process upset at the time of the 10% downward SP change. Additionally, the output trend is rather noisy, indicating excessive amplification of process noise by the controller.

Also Read : Ziegler-Nichols Open-Loop Theory

Ziegler-Nichols closed-loop tuning procedure

Next, the closed-loop, or “Ultimate” tuning method of Ziegler and Nichols was applied to this process. Eliminating both integral and derivative control actions from the controller, and experimenting with different gain (proportional) values until self-sustaining oscillations of consistent amplitude were obtained, gave a gain value of 15:

Ziegler-Nichols tuning

From the trend, we can see that the ultimate period (Pu) is approximately 5.2 minutes in length. Following the Ziegler-Nichols recommendations for PID tuning based on these process characteristics:

Ziegler-Nichols closed-loop

These PID tuning values are quite similar to those predicted by the open loop (“Reaction Rate”) method, and so we would expect to see very similar results:

Ziegler-Nichols closed-loop Formula

As expected, we still see excessive oscillation following a 10% setpoint change, as well as excessive “noise” in the output trend.

Also Read : Ziegler-Nichols Closed-Loop Theory

Heuristic tuning procedure

From the initial open-loop (manual output step-change) test, we could see this process was selfregulating with a slow lag and substantial dead time. The self-regulating nature of the process demands at least some integral control action to eliminate offset, but too much will cause oscillation given the long lag and dead times. The existence of over 1 minute of process dead time also prohibits the use of aggressive proportional action. Derivative action, which is generally useful in overcoming lag times, will cause problems here by amplifying process noise. In summary, then, we would expect to use mild proportional, integral, and derivative tuning values in order to achieve good control with this process. Anything too aggressive will cause problems for this process.

After some experimenting, the values I arrived at were 3 (gain), 5 minutes (integral), and 0.5 minutes (derivative). These tuning values represent a proportional action only one-third as aggressive as the Ziegler-Nichols recommendation, and an integral action about half as aggressive as the Ziegler- Nichols recommendation. The results of these tuning values in automatic mode are shown here:

Heuristic loop tuning procedure

As you can see, the system’s response has almost no overshoot (with either a 10% setpoint change or a 15% setpoint change) and very little “noise” on the output trend. Response to setpoint changes is relatively crisp considering the naturally slow nature of the process: each new setpoint is achieved within about 7.5 minutes of the step-change.

Also Read : Heuristic PID Tuning Theory

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

What is Instrumentation and Control ?
On/off Control Theory
Feedforward Vs Feedback Control
Closed Loop Control System : Boiler Water Level Control System
Basics of Trips, Interlocks, Permissives & Sequences
Example of Feedback System
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

What is Advanced Process Control (APC)?
Design and Implement Motor Control – Electrical Engineering
Switches, Repeaters, Bridges, Routers, Firewalls
Ziegler-Nichols Closed Loop Tuning Procedure
Single Loop Controller Questions
Motor Control Center (MCC) Signal Interface Termination (SIT)
How to choose between PLC and DCS Systems ?
Evaluating Industrial Automation Projects Return on investment (ROI)

Keep Learning

Cascade Control System

Cascade Control

Opposite Acting Valves

What is Split Range Control Loop ?

Loop Splitter Theory of Operation

4-20 mA Loop Splitter

Adaptive Controller Overview

What is Adaptive Control?

Ground Plate

Grounding of Telecommunication Systems

Yokogawa DCS Tutorials - Configuration of Analog Input (Transmitter)

Yokogawa DCS Tutorials – Configuration of Analog Input (Transmitter)

Wellhead Control Panel

Basics of Wellhead Control Panel (WHCP)

Distributed Control System & Motor Control Center Interface Philosophy

Distributed Control System & Motor Control Center Interface Philosophy

Learn More

Power Electronics Objective Questions

Inverters Quality Objective Questions

Flow Switch Principle

In-Line Flow Switch Working Principle and Animation

Loop Power Indicator Principle

Basics of Loop Powered Devices

Closed-tank-DP-Level-Transmitter-with-wet-leg-elevation-zero-direct-mount-Calibration

Closed tank DP Level Transmitter with wet leg elevation zero direct mount Calibration

Types of MCB

Types of MCB

Digital Electronics Multiple Choice Questions

Up Down Counter Objective Questions

Differential Pressure Transmitter Zero Suppression

Basics of DP Transmitter Suppression and Elevation

Impulse Line Purging and Close Coupling

Impulse Line Purging and Close Coupling of Instruments

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?