Reading: Thermocouple Software compensation
Inst Tools > Blog > Temperature Measurement > Thermocouple Software compensation
Last updated: April 20, 2019 5:52 pm
3 Min Read
Previously, it was suggested that automatic compensation could be accomplished by intentionally inserting a temperature-dependent voltage source in series with the circuit, oriented in such a way as to oppose the reference junction’s voltage:
If the series voltage source Vrjc is exactly equal in magnitude to the reference junction’s voltage (VJ2), those two terms cancel out of the equation and lead to the voltmeter measuring only the voltage of the measurement junction J1:
  • Vmeter = VJ1 + 0
  • Vmeter = VJ1
This technique is known as hardware compensation, and is employed in analog thermocouple temperature transmitter designs.
Previously we saw an example of this called an ice point, the purpose of which was to electrically counter the reference junction voltage to render that junction’s voltage inconsequential as though that junction were immersed in a bath of ice-water.
A modern technique for reference junction compensation more suitable to digital transmitter designs is called software compensation:
Instead of canceling the effect of the reference junction electrically, we cancel the effect arithmetically inside the microprocessor-based transmitter. In other words, we let the receiving analog-digital converter circuit see the difference in voltage between the measurement and reference junctions (Vinput = VJ1 − VJ2), but then after digitizing this voltage measurement we have the microprocessor add the equivalent voltage value corresponding to the ambient temperature sensed by the RTD or thermistor (Vrjc):
  • Compensated total = Vinput + Vrjc
  • Compensated total = (VJ1 − VJ2) + Vrjc
Since we know the calculated value of Vrjc should be equal to the real reference junction voltage (VJ2), the result of this digital addition should be a compensated total equal only to the measurement junction voltage VJ1:
  • Compensated total = VJ1 − VJ2 + Vrjc
  • Compensated total = VJ1 + 0
A block diagram of a thermocouple temperature transmitter with software compensation appears here:
SMART Temperature Transmitters
Perhaps the greatest advantage of software compensation is the flexibility to easily switch between different thermocouple types with no hardware modification. So long as the microprocessor memory is programmed with look-up tables relating voltage values to temperature values, it may accurately measure (and compensate for the reference junction of) any thermocouple type.
Hardware-based compensation schemes (e.g. an analog “ice point” circuit) require re-wiring or replacement to accommodate different thermocouple types, since each ice-point circuit is built to generate a compensating voltage for a specific type of thermocouple.
Difference Between 2 wire RTD, 3 wire RTD, and 4 wire RTD’s
Pressure and Temperature Gauges
Spiral Bimetallic Thermometer Principle
Interview Questions on Temperature Measurement
Distributed Temperature Sensors (DTS) in Power Lines
Ambient Temperature Effects on RTD
  • Simon Watah says:
    March 17, 2021 at 8:49 am
    Very helpful knowledge when trying trying to understand how bimex calibrator is connected and used to do function testing on thermocouple.
RTD Wheatstone Bridge Circuits
Thermocouple Calibration
Multiple Position Calibration of Temperature Chamber
What is a Thermocouple ?
Introduction to RTDs
Liquid In Glass Thermometer Principle
Functions of Temperature Detectors
Thermocouple Construction
Thermowell Installation near Critical Equipment
Temperature Calibration Bath
Temperature Calibration Bath Principle
Pneumatic Temperature Transmitter with Sensor Principle
Four Wire RTD Principle
How a 4 Wire RTD Works ?
Head Mount Temperature Transmitter
What is a Head Mount Temperature Transmitter? – Advantages
Temperature-gauge-calibration
Temperature Sensor calibration procedure
RTD Questions & Answers
RTD Questions and Answers
Temperature Gauges and Elements Specifications
Temperature Gauges and Elements : Detailed Specifications
Programmable Read Only Memory Objective Questions – Part 1
Yokogawa DCS CPU
System Cabinet Health Checks – PLC and DCS Industrial Automation
Encoders Objective Questions
Memory Devices Objective Questions – Part 3
Raw Materials in CNC Machine Shop
Most Commonly Used Raw Materials in a CNC Machine Shop
What is a Process Alarm
What is a Process Alarm? Types of Alarms
Optimal Control Systems
Output Regulator & the Tracking Problem
Instrument Process Datasheet
Why is an Instrument Process Datasheet Required?