Reading: How to Operate a Group of Induction Motors using PLC Logic?
Inst Tools > Blog > Electrical Basics > How to Operate a Group of Induction Motors using PLC Logic?
We will discuss how to make a PLC logic that could handle and control a group of induction motors smoothly and without any problems.
Last updated: January 28, 2023 11:44 am
Hussien Ghareb
Electrical Basics PLC Tutorials
The induction motor is one of the significant elements of any electrical system (production line), as its low costs, operation in a wide range of industrial conditions, and finally, the simple design and rugged construction make them the best in use.
Induction Motors PLC LogicExample For “Operation of Three Induction Motors”Programming of PLC Code
But as we discussed in the previous article earlier, there are some problems that occurred with the miss operating a group of Induction Motors.
So, in this lesson, we will discuss how to make a PLC logic that could handle and control a group of induction motors smoothly and without any problems.
Here we will make a PLC program that can handle the operation of three induction motors that is needed to be operated in a specific order.
Once the operator presses the start push button the first induction motor will run and after five seconds the second motor will run finally and after additional five seconds the third motor will take the order to run.
After the three motors are running and once the operator presses the stop push button the three motors will stop (with the same periods between each motor) but with an opposite sequence as shown in Fig. (1).
Figure 1
Here we are dealing with SIEMENS PLCs (S7-1200) using the ladder diagram.
Join Siemens PLC Course
Siemens PLC Tia Portal Training Course
Network 1 – First Motor Start Stop Logic
Once the operator presses the start push button as we can see in Fig. (2), (I0.0) will energize the output coil (Q0.0) that is responsible for turning the first induction motor on.
First Motor Start Stop PLC Code
Figure 2
Network 2 – Second Motor Delay Logic
Then after the first motor is turned on (Q0.0), it will start a delay timer (DB5) with a preset time of 5 Seconds.
Network 3 – Second Motor Start Stop Logic
As we can see In Fig. (3) the output of the delay timer (M0.0) will be responsible for turning the second induction motor on (Q0.1), then the motor will latch on itself and it will resume running.
Motor Delay PLC Programming
Figure 3
Network 4 – Third Motor Delay Logic
Then after the second motor is turned on (Q0.1) (NOTE: stop push button is NC) and we did not press the stop push button, the second motor coil (Q0.1) will start a delay timer (DB6) with a preset time of 5 Seconds. As shown in Fig. (4)
Network 5 – Third Motor Start Stop Logic
As we can see In Fig. (4) the output of the delay timer (M0.1) will be responsible for turning the third induction motor on (Q0.2), then the motor will latch on itself and it will resume running.
PLC Induction Motors Start Stop Logic
Figure 4
Once the operator presses the stop push button as we can see in Fig. (4), immediately (I0.1) will de-energize the output coil (Q0.2) that is responsible for turning the third induction motor off.
Network 6 – Pressing Stop Logic
Then as shown in Fig. (5) when the operator presses the stop push button, (I0.1) will energize a marker (M0.4)
Pressing Stop Button PLC Program
Figure 5
Network 7 – Second Motor Stoppage Delay Logic
Then as shown in Fig. (6) when (M0.4) is energized, it will start a delay timer (DB7) with a preset time of 5 Seconds.
The output of the delay timer (M0.2) will be responsible for turning the second induction motor off (Q0.1) as shown in Fig. (3).
PLC Operate Group of Induction Motors Simultaneously
Figure 6
Network 8 – First Motor Stoppage Delay Logic
In addition to de-energizing the second motor (Q0.1), (M0.2) will start a delay timer (DB8) with a preset time of 5 Seconds.
The output of the delay timer (M0.3) will be responsible for turning the first induction motor off (Q0.0) as shown in Fig. (2).
  • Automation Documents
  • Delta PLC & VFD Modbus
  • Compare PLC and SCADA
  • PLC and DCS System Checks
  • DCS System Maintenance
Structured Text in PLC: Parking Information Systems
What are User Defined Function Blocks in PLC?
Difference between DCS, PLC, and RTU ?
Overview of SIEMENS PLC – S7-1500, S7-1200, S7-400, S7-300
What is a Bus Coupler in Electrical Panel?
Components of SCADA
How-to do Security of SCADA Systems?
User Defined Data Types (UDT) – Purpose, Need, Tutorial
Motor Speed Control using VFD and PLC Programming
Conveyor Control with Main Motor and Backup Motor
Download Free Robotics Software
Step by Step Guidelines to Download Free Robotics Software
Difference between Stepper Motor and DC Motor
different PLC brands of Distributed IO
What is Distributed IO? – Decentralized Peripherals in PLC
PID block from the PLC library
How to Configure PID Controller in Various Schneider PLCs?
Using Clock Memory Bits in TIA Portal - Siemens PLC
PLC Program for Password Management using Structured Text
Siemens Tia Portal PLC Training Course
PLC Project Examples for EcoStruxure Machine Expert
Analog to Digital Converters Objective Questions
Transformers Questions & Answers Part-4
Interview Questions and Answers
Electrical Machines Interview Questions and Answers
Ring Counter Objective Questions
Process Pressure Measurement Objective Questions