Reading: What happen When Synchronous Generator loss Excitation
Inst Tools > Blog > Electrical Machines > What happen When Synchronous Generator loss Excitation
Last updated: April 25, 2016 3:15 pm
Electrical Machines
2 Min Read
During normal operation of the Synchronous Generator or Alternator excitation to the rotor is provided by the small DC generator running on the same shaft along with main generator. When synchronous generator delivering power to the grid or load it delivers both real power and reactive power to the system. Reactive power is the magnetizing power which helps to deliver the real power from source to the load and also reactive power helps to improve the voltage of the system. Almost all the loads (except capacitance loads) in the power system draws reactive power from system. Alternators, synchronous condensers and capacitor banks connected in the power systems are the only sources of reactive power.
Real power delivered by the generator (MW output power) is governed by the prime mover and the Reactive power delivered (MVAR output ) is governed by the field excitation. When field excitation to the synchronous generator is lost then synchronous generator operates as induction generator and instead of delivering reactive power it absorbs the reactive power from the system as much as 2 to 4 times the generator’s rated load. However the real power (MW output) delivered by the induction generator will remain almost the same as this is controlled by the prime mover.But loss of generator’s reactive power in the system may cause instability to the system. Also, as alternator is operating as induction generator, high currents are induced in to the rotor teeth and wedges and may damage the rotor of the generator. However large alternators are designed to withstand this induced currents.
Immediate tripping of alternator in the case of loss of excitation is not necessary unless the terminal voltage of the generator falls below desired limit due to voltage collapse. Loss of excitation relay (40G) is used for sensing the loss of excitation.
Advantages of Hydrogen cooling in Synchronous Generators
Zigzag Transformers Theory
Stepper Motor Basics, Types, Modes, Wiring, Questions
DC Motor Speed Control
Faults in a Transformer
AC Motor Speed Control
Advantages and Disadvantages of Squirrel Cage Induction motor
Transformer Open and Short Circuit Tests
Difference between Permanent Magnet BLDC and DC Motor
Why Starting Current of Induction Motor is High
Synchronous Generator Salient Pole vs Non Salient Pole
Importance of Hysteresis Loop
Why rating of Synchronous Generators and Alternators in MVA or KVA
AC Induction Motor Construction
Basics of AC Induction Motors
Alarm Trip for 24v DC Loop
Advantages & Disadvantages of Synchronous Motors
Advantages & Disadvantages of Variable Speed Drives
Thermowell-Insertion-and-Immersion-Length
What is a Transformer Tap Changer
Metering pumps
Metering Pumps
What is a transformer tap changer?
Types of Transfomer Cooling Methods
Electrical-Switches-Working-Animation
Difference between Star and Delta Connections
Allen Bradley RSLogix 500 PLC Programming
Control Valves Classification
Classification of Control Valves
Use of Regions in SCL Language
Gearbox within week Failing Journal Bearing upset Plant Operations
Capping Machines
Capping Machine – 5 Aspects of Control Systems and Automation
Electrical Machines Loss Dissipation Quiz
Series-Wound DC Generator Principle
Series-Wound DC Generators
Transformers Coolers Weld Joints Oil
Transformers Coolers Weld Joints Oil Oozes Were Eye Sores