Reading: Fire and Gas System Loop Checks Procedure
Inst Tools > Blog > Fire & Gas System > Fire and Gas System Loop Checks Procedure
Guidelines to be followed by F&G Engineer during Fire and Gas System Loop Checks Procedure. Read this article on Fire Alarm System commissioning.
Last updated: August 28, 2020 10:25 am
Fire & Gas System
3 Comments
Guidelines to be followed by Panel Engineer during Fire and Gas System Loop Checks:
1. Location of the FGS Tag no. to be checked (As per Drawing, it should be on that particular area or near the particular equipment)
2. Tag number & Description of the Tag to be checked.
3. Range of that Particular instrument to be checked. (As per Instrument index)
4 5. Color of the Display (Normal: Green, Abnormal: Red blinking; Acknowledged Alarm: Static Red; Fault value: Yellow)
6. For Detectors – The checks will be done for 0%,20%,50% & 100% of the total range. 20% value will appear in Amber Color. 50% value will appear in Red color.
7. For Detectors & MCP : Normal, Abnormal & DCS Alarm values, if any, & Fault alarm to be incorporated & to be checked by simulating from field & alarm to be checked in Alarm summary.
8. For Detectors, Hooters, Beacon : Normal, Abnormal & Fault alarm to be simulated & checked. And also confirm with Field Engineer that Sound was more Audible & Beacon bulb glowing was bright. Gas Beacon & Gas Hooter will appear in Amber Color when there is a alarm in Graphics. Fire Beacon & Fire Hooter will appear in Red Color.
9. For Building Alarms from FAP (Fire Alarm Panel): Normal, Abnormal & Fault alarm simulation to be checked.
10. If there is any deviation from the above, please write your observations in Loop Test Report & DPR (Daily Progress Report).
11. Mark in F&G layout P&ID after loop check.
Also Read: How to do logic Checks
Guidelines to be followed by Field Engineer during Fire and Gas System Field Loop Checks:
1. Location of the F & G Device instruments (As per Drawing, it should be on that particular area or equipment)
2. Position of that F & G Device in field to be verified. (For eg: MCP are to be placed more than 5 metres away from Hydrocarbon area)
3. Name plate of that instruments (Should match with Drawing)
4. For Detectors, the checks will be done for 0%, 20%, 50% & 100% of the total range. The readings displayed to be counterchecked with the person on DCS.
5. For Beacon & Hooters, it will be simulated from Control Room, Visual lamp flashing to be checked in field (Gas Beacon – Yellow color & Fire Beacon – Red color).
6. For Hooters, it will be simulated from Control Room, Audible Sound to be checked in field. Eg. If they are simulating Gas Hooter from Control, only Gas Hooter in Field should sound. Both Hooter – Gas & Fire Hooter, sounds should be different.
7. If there is any deviation from the above, please note & inform your observations to the Person in Control Room, so that he will write in Loop Test Report & DPR (Daily Progress Report).
Note: Colors, graphics, Philosophies, etc… may change from industry to industry.
Also share any points if we missed in the above list via comments section.
Also Read: How to do DCS/Field Loop Checks
Fire and Gas system Audible and Visual Alarms
Smoke Detector Testing Procedure
Gas Detectors Standards
MOS Type Gas Sensor Principle
Factors for Setting Alarm Levels on Toxic Gas Detectors
3 Comments
  • Ramu says:
    March 18, 2016 at 6:33 am
    Thank you friend.
  • alam says:
    February 7, 2019 at 2:05 am
    please make a note for boilers operation and maintenance
  • ahmed messallam says:
    October 4, 2022 at 1:15 pm
    good information, thank you.
Basics of Fire Detection System
Gas Detection Excel Converters
Basics of Fire Detection and Alarm System
What are Fire Branches?
What is Photoionization Detector (PID)?
What is a Fire Pump? – Definition, Principle, Types, Comparison
Importance of Fire & Gas Detection System
Which One is Best – Conventional or Addressable Fire Alarm System?
Explosive Limit in Fire and Gas System
What is an Explosive Limit? – Lower Explosive Limit (LEL)
Argonite/CO2 Flooding System Master & Slave Cylinder Operation
Fixed Gas Detectors vs. Portable Gas Detectors
Gas detection system Interview Questions
Interview Questions on Gas detection System
fire alarm system operation
What is Fire Alarm System?
Gas Detectors Location Installation
Gas Detectors Installation Techniques
Quartzoid Bulb Detector Working Principle
Fire Water Sprinklers Working Principle
Infrared Gas Detectors Principle
Infrared Gas Detectors Working Principle
RTD Construction
Introduction to RTDs
Electronic Pressure Sensor with Bourdon Tube and LVDT
What is a Compressor
What is a Compressor? Types of Compressors
running two single-phase induction motors sequentially
Control Two Motors in Sequence after Time Delay – Circuit, Operation
Robotic Process Automation
What is Robotic Process Automation? Advantages, Applications
Temperature Measurement Objective Questions
gate-valve-principle-animation
Basics of Gate Valves
Speed Control of DC Motors Quiz