Reading: Diagnosing Electric Motor Circuit
Inst Tools > Blog > Practical Questions > Diagnosing Electric Motor Circuit
Last updated: January 8, 2020 2:41 pm
Practical Questions
2 Min Read
Suppose the electric motor refuses to run when the “Run” pushbutton switch is pressed. A technician begins diagnosing electric motor circuit following the steps shown (in order):
  • Test 1: Measured 12 volts DC between points C and D, with “Run” switch pressed.
  • Test 2: Measured 0 volts DC between points A and C, with “Run” switch unpressed.
  • Test 3: Measured 12 volts DC between points A and B, with “Run” switch pressed.
  • Test 4: Measured 12 volts DC between points E and F, with “Run” switch pressed.
  • Test 5: Measured infinite ohms between points E and F, with “Run” switch unpressed.
Diagnosing the Electric Motor Circuit
Identify any useful information about the nature or location of the fault derived from the results of each test, in order of the tests performed.
If the test is not useful (i.e. provides no new information), mark it as such. Assuming there is only one fault in the circuit, identify the location and nature of the fault as precisely as you can from the test results shown above.
Solution:
The fault is an “open,” between points E and F.
Share your answers & explanations.
Credits: Tony R. Kuphaldt
  • AC Motor Theory
  • Types of AC Generators
  • AC Generation Analysis
  • Series-Wound Motor
  • DC Generator Internal Losses
Is it Possible to Measure Liquid-Liquid Level Interface using Float?
Which Instrument is at Fault in this System?
As per Process Conditions, Find out the Circuit Components Status ?
Type E thermocouple Calculations
Solenoid-controlled Valve Problem
Tank uses 3 Pressure Transmitters to Measure Level & Density
How to Connect Proximity Switch (Sink Type) to Make LED ON ?
Liquid Level Switch Control Logic
Solenoid Valves Questions & Answers – 2
Resistance Temperature Detector (RTD) Questions – 1
Stripper Overhead Temperature Control System
Problem on Solar Hot Air Collector and Variable Speed Fan
Questions on Pressure Transmitter Calibration Setup
Calculate Density and Specific Gravity
Which instrument is faulty
Which Instrument is Faulty? Transmitter, Recorder, or Controller
How Much Pressure indicated by Micromanometer
How Much Pressure Indicated by Micromanometer?
Identify the Pressure Gauge Error
Galileo thermometer Principle
Galileo Thermometer
Differential Capacitance Pressure Sensor Circuit
Pressure gauge mechanism
How Measurement Span of Pressure Gauge Could be Changed?
Relay ladder diagram example
How to Draw a Schematic Diagram ?
Pneumatic-Level-Transmitter-Value-Struck
Pneumatic Level Transmitter Value Struck?
PLC Programming Sequence Logic
PLC Programming to Control Lights in a Sequence
Gate Valve
How Gate Valves Work ?
What is Hot Water Recirculation Loop
What is Hot Water Recirculation Loop? Advantages & Design
Safety PLC Coding Practices
Safety PLC Coding Practices – Programming Recommendations
Control Valve in Last Position
Control Valve Fail Safe Action
Pressure gauges with capsule elements
Pressure Gauges with Capsule Sensor Principle