Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Capacitance Level Switch Calibration
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Calibration > Capacitance Level Switch Calibration

Capacitance Level Switch Calibration

Last updated: April 27, 2019 12:16 pm
Editorial Staff
Calibration Guest Articles
3 Comments
Share
7 Min Read
SHARE

Level Measurement: In industry, liquids such as water, chemicals, and solvents are used in various processes. The amount of such liquid stored can be found by measuring level of the liquid in a container or vessel. Level sensors detect the level of substances like liquids, slurries, granular materials, and powders.

Contents
Capacitance Level Switch CalibrationWiring Connection:Calibration:

A Capacitance switch designed for single point level detection in both solids and liquids.

Capacitance Level Switch Calibration

Every material has a relative permittivity or dielectric constant. A basic capacitance switch uses this dielectric constant to complete a capacitance circuit between a sensor and a reference. The presence of a material creates a shift in the received capacitance causing the switch to activate. While these basic capacitance style switches are useful..

Capacitance level transmitters use the principle of the dielectric plate measurement technique to determine a level or interface measurement. A capacitor is formed when a level sensing electrode is installed in a vessel. The metal rod of the electrode acts as one plate of the capacitor and the tank wall (or reference electrode in a non-metallic vessel) acts as the other plate.

As level rises, the air or gas normally surrounding the electrode is displaced by material having a different dielectric constant. A change in the value of the capacitor takes place because the dielectric between the plates has changed. RF (radio frequency) capacitance instruments detect this change and convert it into a proportional output signal.

The capacitance relationship is illustrated with the following equation:

C = 0.225 K (A / D )

Where: C = Capacitance in picofarads

K = Dielectric constant of material

A = Area of plates in square inches

 D = Distance between the plates in inches

Capacitance Level transmitter & Switch Principle

In actual practice, capacitance change is produced in different ways depending on the material being measured and the level electrode selection. However, the basic principle always applies. If a higher dielectric material replaces a lower one, the total capacitance output of the system will increase. If the electrode is made larger (effectively increasing the surface area) the capacitance output increases; if the distance between measuring electrode and reference decreases, then the capacitance output decreases. Level is proportional to the capacitance measured. Since the capacitance is dependent on a stable dielectric of the medium throughout the height of the level column, the overall accuracy of either level or interface measurement will be impacted if the dielectric constant changes.

Capacitance-Level-Transmitter

Installation instruction:

To install the level switch consider the following points for correct level measurement:

  1. Keep the sensor at least 50 mm (2″) away from any nozzle or tank wall.
  2. If multiple units are used, allow at least 100 mm (4″) between them, to prevent interference (mount diagonally if space is restricted).

Level Switch MOUNTING_INSTRUCTION

High level alarm

  1. Normally mounted into the vessel top
  2. Through the tank wall at the detection level

Low level alarm

  1. Mounted through the tank wall at the detection level

Process Connection:

  1. Keep unit out of path of falling material, or protect probe from falling material.
  2. Avoid areas where material build up occurs.

process_connection_for_level_switch

Wiring Connection:

Consider a Level Switch of siemens make for following procedures :

level switch wiring connection

Calibration:

After properly mounted apply power to the unit. The green LED (L3) glows, indicating the unit is powered and use for operation. Use the potentiometers P1 and P2 to adjust the alarm delay and set point.

Follow the setup procedure for the application that most closely describes your operation:

Condition for various type process materials:

Application Material Setup Conditions
General • Dry solids

•Low viscosity liquids

Sensor uncovered; min. 100 mm (4″) free space all around
Demanding • Hygroscopic / wet solids

•High viscosity and high conductivity liquids

Sensor immersed then uncovered; but retaining max. possible material buildup
Interface detection • Liquid A / liquid B

•Foam / liquid

immerse sensor in whichever material has lowest dielectric constant

Calibration for general applications (Failsafe low, no delay) :

  1. Ensure the green power LED L3 is on.
  2. Set DIP switches S1 to S4 to OFF.
  3. Set DIP switch S5 ON (set-up mode).
  4. Ensure the probe is uncovered. If the yellow sensor status LED L1 is not on, turn the trip-point potentiometer P2 counter-clockwise until it just turns on.
  5. Turn the trip-point potentiometer P2 clockwise until LED L1 just turns off.
  6. Set DIP switch S5 to OFF (run mode).

Calibration for demanding applications (Failsafe low, no delay)

  1. Ensure that the green power LED L3 is on.
  2. Set DIP switches S1 to S4 to OFF.
  3. Set DIP switch S5 to ON (set-up mode).
  4. Turn the delay potentiometer P1 fully counterclockwise.
  5. Adjust the material level of the process so that the sensor is immersed.
  6. Adjust the material level of the process so that the sensor is uncovered, but retains as much buildup of material as possible on the sensor.
  7. If the yellow sensor status LED L1 is not on, turn the trip point potentiometer P2 counter-clockwise until it just turns on.
  8. Turn the trip point potentiometer P2 clockwise until LED L1 just turns off.
  9. Set DIP switch S5 to OFF (run mode). 

Calibration for interface detection (Failsafe low, no delay) :

  1. Ensure that the green power LED L3 is on.
  2. Set DIP switches S1 to S4 to OFF. 3. Set DIP switch S5 to ON (set-up mode).
  3. Turn the delay potentiometer P1 fully counter-clockwise.
  4. Adjust the material level of the process so that the sensor is covered by the material with the lowest relative dielectric constant.
  5. If the yellow sensor status LED L1 is not on, turn the trip point potentiometer P2 counter-clockwise until it just turns on.
  6. Turn the trip point potentiometer P2 clockwise until LED L1 just turns off. 8. Set DIP switch S5 to OFF (run mode).

Note : Procedures vary from model to model.

Reference : Siemens Manuals

Article by :
Ashish Agrawal
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

What is Field Transmitter Damping ?
Bently Nevada Vibration Probes Functional Testing
PLC Program for Positive Edge Pulse Output for One Scan Cycle
Instrumentation Engineer’s Calibration Mistakes
Hydrogen Sulfide Gas Detector Calibration Procedure
How to Calibrate Oxygen Analyzer? – O2 Sensor Testing Procedure
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
3 Comments
  • Minaz says:
    December 9, 2017 at 5:13 pm

    Sir articles are too informative..
    I want to know whether it is possible to download the article from the app for future reference

    Reply
    • S Bharadwaj Reddy says:
      December 10, 2017 at 2:47 am

      Hi, ” Instrumentation Tools ” Android App has inbuilt save option for offline read.

      Reply
  • Mohammad says:
    September 14, 2018 at 2:01 pm

    I have a flowserve positiner named logix 3200. It’s hunting and not operating from dcs. Pls tell me the solution.

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Specific Conductance Calibration Procedure
Selection of Weighing Balance and Weight for Calibration
Differential Pressure Switch Calibration Procedure
Selection of Industrial Temperature Calibrator
Calibration Procedure of Weighing Balance and Common Mistakes
Difference between Calibration and Ranging
Difference between Intrinsic Safe and Non-Intrinsic Safe Cables
Prover Tank Calibration and Mass Flow Meter Verification Procedure

Keep Learning

Gas Detectors Calibration

Calibration of Gas Detectors

Multiphase Flow Meter Calibration Procedure

Multiphase Flow Meter Calibration Procedure

DP Transmitter Capillary arrangement

DP Transmitter Interface Level Measurement Principle, Limitations, Selection, Installation, Design & Calibration

Smart Transmitter Calibration Tutorial

Smart Transmitter Calibration Tutorial Part 1

DP type Flow Transmitter Calibration

DP type Flow Transmitter Preventive Maintenance and Calibration

dead-weight-tester-principle

What is a Dead Weight Tester?

DP Diaphragm Capillary Seal Level instrument

DP Diaphragm Capillary Seal Level instrument Calibration Procedure

Calibration MCQ - Terminology and Glossary Questions

Calibration MCQ – Terminology and Glossary Questions

Learn More

Tank car bonding at siding

Electrical Static Grounding Techniques

Electrodynamometer Movement Principle

Electro-Dynamo Meter Movement

Characteristics of Transducers Objective Questions

Characteristics of Transducers Objective Questions

High Level Alarm of Distillation Process

Investigate High Level Alarm of Distillation Process

Overview of Industrial Control Systems

Overview of Industrial Control Systems

Ground Fault Versus Short Circuit

Difference Between Short Circuit and Ground Fault

what-is-gas-metering-system

What is Gas Metering System?

Can a PLC Function Without an HMI or SCADA

Can a PLC Function Without an HMI or SCADA?

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?