Reading: Motor Trip Logic using PLC Programming
Inst Tools > Blog > PLC Tutorials > Motor Trip Logic using PLC Programming
Last updated: April 20, 2021 7:22 am
PLC Tutorials Practical Questions
10 Comments
1 Min Read
This PLC is being used to start and stop an electric motor, and also to shut it down automatically if any of three “shutdown” conditions occur:
  • Excessive vibration
  • Overcurrent (overload heater contact)
  • High winding temperature
The status of each shutdown contact is as follows:
  • Vibration contact: closed when okay, opens when vibration becomes excessive
  • Overload contact: closed when okay, opens when overloaded
  • Temperature contact: open when okay, closes when hot
Draw a PLC ladder-logic program to start and stop this motor.
Be sure to make the program latching so that the operator does not have to hold the Start button to keep the motor running.
Answer:
Do you find any mistakes in the logic? Share with us through comments.
PLC Motor Interlocks
Share Your Answer / Comments
Credits : by Tony R. Kuphaldt – under CC BY 1.0
For More PLC Questions : CLICK HERE
How to Choose a PLC for New Project? – Criteria for Selection of PLC
PLC Application for Stamping Operation – Example Programming
PLC FBD Program for Bottle’s Capping with Rotating Mechanism
PLC Power Supply and Operating Voltages
10 Comments
  • amani says:
    April 17, 2018 at 2:34 pm
    fantastic title
    thanks
  • Anthony says:
    September 9, 2019 at 3:43 pm
    This is indeed a powerful source of information. I am truly humbled.
    Thank you
    Maphalla MA
  • Francis Usen says:
    November 6, 2019 at 1:47 am
    God bless
    November 6, 2019 at 2:07 am
    sorry, X1, X2, X3 should be NC Contacts here.
    • Umesh says:
      April 19, 2021 at 4:50 pm
      True…contacts must be closed there…open for TS
  • morshadul haque says:
    December 5, 2019 at 2:15 pm
    good idea
  • Man prasad shah says:
    February 13, 2022 at 2:44 pm
    X0,X1,X2,X3, NEED TO NC contact
  • DINESH KUMAR SINGH says:
    March 14, 2022 at 10:03 pm
    X1, X2, X3 all is NC Contact.
  • Dheeraj R says:
    January 16, 2023 at 4:25 pm
    Stop , vibration, overload should be NC
  • Ahmed Olalekan says:
    October 6, 2023 at 3:08 pm
    No they should not. They are NC instruments yes but if you keep as NC in logic motor will not start as they will turn open in the logic
Single Loop Controller Questions
DCS Commissioning Steps
Something is Wrong with Strain Gauge Bridge Circuit
PLC Multiple Outputs Configuration
Upgrading and Migration of PLC Systems
Practical Control Systems Questions & Answers - 2
Practical Process Control System Questions & Answers – 2
PID Setup
PID in Studio 5000
Creating Logic in Intouch Using Scripting
Create Logic with InTouch Scada using Scripting
Comparison of Control Loops - Open, Closed, Cascade, Feedforward, Ratio
Comparison of Control Loops – Open, Closed, Cascade, Feedforward, Ratio
Shutdown Motors in Timed Operation PLC Program
Water Fountain Control Logic
Water Fountain Control Logic – PLC Exercises and Solutions
SCADA Interview Questions
Ripple Counter Objective Questions
Time Response Analysis
State Variable Analysis – Part I
How to Calibrate Load Cells
How to do Control Valve Sizing
How do you do control valve sizing in Layman’s terms?
Optical Fiber Cable - SC and ST Optical Fiber Connectors
Optical Fiber Cable – SC and ST Optical Fiber Connectors
Radiation Level Measurement
Rewire Tool
What is Rewire Tool in Simatic Manager?
Analog Electronics Objective Questions – Set 10