Instrumentation Engineer’s Calibration Mistakes
Error When Attempting to Reverse the Range
In some applications, particularly DP level, it is necessary to reverse the range such that the LRV > URV.
For instance, the range may have been set -87 to -1 mbar initially, but the application may actually require the range to be -1 to -87 mbar. That is the range has to be reversed:
Before :
LRV = -87 mbar  &  URV = -1 mbar
After Change :
LRV = -1 mbar  &  URV = -87 mbar
To make this range change the technician would typically make the mistake of directly enter -1 mbar for LRV which would be rejected since both URV and LRV would then be -1 mbar leaving a span of 0 mbar which would violate the minimum span.
Or, the technician would attempt to directly enter -87 mbar for URV which would also be rejected since both URV and LRV would then be – 87 mbar also violating the minimum span.
The solution is to first enter an intermediate value. For instance, setting the LRV to -40, then setting URV to -87, and lastly setting LRV to the final -1 mbar.
The same procedure applies if the sensor trim points are to be reversed.
4-20 mA Range MismatchÂ
If the range set in the transmitter does not match the range in the DCS, alarms, controls, and indication will not function correctly.
Therefore it is important to document any range changes such that the correct range is set when transmitters are replaced.
In this above example a mismatch in LRV results in erroneous indication.
Corrupting the range to make 4-20 mA right
Don’t use range setting to correct a sensor error. For example, a 4-20 mA/HART pressure transmitter ranged 0 to 100 inH2O may due to mounting position get a shift in reading of 1 inH2O.
The analog output will be 4.16 mA when no pressure is applied, making the field indicator or HMI show 1 inH2O.
A common mistake is to isolate, equalize, and vent the manifold and click the ‘Set PV LRV’ command in the device management software or handheld field communicator, or pushing the ‘zero’ and button on the device thus changing the range bringing the analog output to 4 mA.
However, checking the PV in the device management software or local transmitter indicator will reveal the sensor reading with no pressure applied is still 1 inH2O and the range is changed to 1 to 101 in H2O. Two wrongs appear to make a right.
The correct way to correct for shift or drift is to do a sensor trim.
Corrupting the sensor reading to make 4-20 mA right
Don’t use sensor trim to cancel a wet-leg. For example, a 4-20 mA/HART pressure transmitter ranged 0 to 100 inH2O may when mounted below the tank read 1 inH2O.
The analog output will be 4.16 mA when the level is zero (at the tank datum point), making the field indicator or HMI show 1 inH2O.
A common mistake is to click the ‘Zero Trim’ command in the device management software or handheld field communicator thus changing the sensor reading bringing the analog output to 4 mA.
However, if the 4-20 mA/HART pressure transmitter is isolated and vented, and the PV checked in the device management software or local transmitter indicator, it will show the sensor reading with no pressure applied is -1 inH2O. Two wrongs appear to make a right.
The correct way to cancel a wet leg is to set the range.
Non-interactive zero and span
One of the major time saving benefits that came with microprocessor-based transmitters was non-interactive zero and span:
When lower range value is set to applied input, the span (i.e. the difference between upper range value and lower range value) is maintained. That is, the upper range value is shifted by the same amount as the lower range value.
For instance, if the original range was 0-100 kPa, and lower range value is set to applied input when the applied input is 20 kPa, the new range will be 20-120 kPa, maintaining the original span of 100 kPa.
That is, the upper range value was also shifted by 20 kPa just like the lower range value.
However, if upper range value is set to applied input, the lower range value zero) is not changed.
For instance, if the original range was 0-100 kPa, and upper range value is set to applied input when the applied pressure is 80 kPa, the new range will be 0-80 kPa, maintaining the original zero of 0 kPa. That is, the lower range value was not shifted.
That is, changing the zero does not affect the span, changing the span does not affect the zero. This is non-interactive zero and span.
Article Source : Eddl
No Words…. Simply the Best. Excellent Articles. Thank you for sharing.
Keep up this excellent work of sharing
Good info
Excellent!… these are real world problems that have many technicians confused about proper calibration procedures, especially since the advent of micro-processor based instrumentation. In the old days of mostly pneumatic instrumentation, those problems didn’t exist because of the use of mechanical elevation and suppression. Today’s modern technology require a lot more training in the installation, setup and calibration of instrumentation. As a side note, I would also say that more technical education in math and physics are required as well.
Thanks for all you do S Bharadwaj Reddy to promote the knowledge base of instrumentation technology.
Thank you for your information
Thanks