Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Control Valve Stroke Test Procedure
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Calibration > Control Valve Stroke Test Procedure

Control Valve Stroke Test Procedure

Last updated: May 16, 2021 9:49 pm
Editorial Staff
Calibration Control Valves
2 Comments
Share
4 Min Read
SHARE

What is Control Valve?

Control valves are used to automatically/manually regulate process variables (pressure (Pressure, Flow, Level, Temperature, etc.) in the process area.

Contents
Equipment Setup:Control Valve Stroke Test ProcedureCalibration Certificate of Control Valve

They are available in various classes as per requirement from PN16 to 1000. The Control Valve is the Final control element that is responsible for controlling the process parameters.

Symbol of Control Valve

Control Valve Symbol

Control Valve Consists of the following elements:

1. Actuator

2. Positioner

3. Valve Body

Main Parts of Control Valve

Actuator:

The Actuator is the Upper Portion of the Cylinder, which allows the diaphragm to move the valve steam upward and downward.

Positioner:

The Positioner is nothing but an advanced I to P converter, which converts the 4-20mA signal to Pneumatic 3-15Psi, and allows the stem of the actuator for the movement to and fro.

Valve Body:

Valve body manufacturing depends on the temperature and pressure in the line. The material of the valve body may be Forged carbon, SS316, SS314, Casting, etc.

Master Equipment:

  • Universal Calibrator
  • Wire
  • Multimeter

Equipment Setup:

The Control Valve Stroke Test Procedure

Control Valve Stroke Test Procedure

1. Assume the valve is a 4-20mA operated pneumatic valve. It also has a 4-20mA valve position feedback output.

2. Connect the universal calibrator (or source) to the input of the valve.

3. Connect the multimeter at the valve position feedback output as shown in above the setup figure.

4. Select the Source function in universal calibrator and the knob will help to vary the mA (4 to 20mA).

5. Select 4mA in the calibrator (also called as source meter). The control valve will show a 0% valve position. We can verify the valve position on the scale provided on the control valve.

Also, the valve has 4 – 20mA output which indicates valve position feedback. We connected a multimeter to measure this valve position feedback. The valve position feedback range is 0 to 100 percent which is equivalent to 4 to 20mA. In this case, the multimeter will show 4mA.

6. Now increase the current (mA) in the calibrator from 4mA to 8mA. Now the valve will travel from 0% to 25%. The multimeter will show 8mA valve travel position feedback (25%).

7. Now increase the current (mA) in the calibrator from 8mA to 12mA. Now the valve will travel from 25% to 50%. The multimeter will show 12mA valve travel position feedback (50%).

8. Now increase the current (mA) in the calibrator from 12mA to 16mA. Now the valve will travel from 50% to 75%. The multimeter will show 16mA valve travel position feedback (75%).

9. Now increase the current (mA) in the calibrator from 16mA to 20mA. Now the valve will travel from 75% to 100%. The multimeter will show 20mA valve travel position feedback (100%).

10. Now we tested the control valve from 4mA to 20mA upward direction. Now repeat the same in downward direction i.e. from 20mA to 4mA in steps.

11. Note: While sourcing you can view the Feedback on multimeter these will be nearby reading to source mA.

12. Now we completed the upward test from 4mA to 20mA. Repeat the same steps in a downward direction also i.e. from 20mA to 4mA in steps.

Calibration Certificate of Control Valve

Find the Calibration Certificate for your reference.

Calibration Certificate of Control Valve

Author: Jadhav Amit R

Read Next:

  • Valve Partial Stroke Test
  • Valve Position Indication
  • Calibration of Control Valve
  • How to Select a Valve?
  • Electrical Motor Actuator
  • Valve Positioners Loop
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Globe Valve Body Design
DP Diaphragm Capillary Seal Level instrument Calibration Procedure
Basics of Globe Valves
Control Valves Theory
Difference between Calibration and Ranging
Dissolved oxygen probe calibration procedure
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
2 Comments
  • RAPOLU JAGAN MOHAN RAO says:
    April 28, 2020 at 11:23 am

    Mr. Jadhav Amit’s article on the Control valve stroke test is very informative.

    Reply
  • okudor Ovie says:
    August 19, 2020 at 11:28 pm

    An informative piece.

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

How is Pressure Drop Calculated through a Valve ?
Basics of Butterfly Valves
Temperature Standards
H & B Gas Analyzer Principle and Calibration Procedure
What is Ball Valve ?
Stability and Uniformity of Temperature Bath
Fundamentals of Valves and their Types
Types of Calibration

Keep Learning

Selection of Master Instrument for Calibration

Selection of Master Instrument for Calibration

Common Mistakes in Dead Weight Tester

Common Mistakes to Avoid When Using Dead Weight Tester

Valve Basics

Basics of Control Valves

Butterfly valve Principle

Short Notes on Different Valve Types

Snap Acting Relay Working Principle

Snap Acting Relay Working Principle

Valves Legend P&ID

Comparison of Gate Valves and Globe Valves

As-Found and As-Left data during Calibration

Why it is important to note As-Found and As-Left data during Calibration?

Electropneumatic Valve Positioner Working Principle

Electro Pneumatic Valve Positioner Schematic & Principle

Learn More

Smart HART Transmitter

Analysis of HART communicator and Smart HART Transmitter

Difference between Accuracy, Tolerance, Uncertainty, and Error

Difference between Accuracy, Tolerance, Uncertainty, and Error

Turbidity Sensor Calibration Procedure

Turbidity Sensor Calibration Procedure

Ratio control

What is Ratio Control ?

Electric Circuits Objective Questions

Electric Circuits Objective Questions – Set 5

DP-Level-Transmitter-Diaphragm-with-capillary-tube-type

DP Level Transmitter Calibration for Diaphragm Seal with Capillary

CONTROL VALVE CHARACTERISTICS

Difference between Quick Opening, Linear & Equal Percentage Control Valve characteristics

Sugar Plant - Automatic Control of Massecuite Feed

Sugar Plant – Automatic Control of Massecuite Feed

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?