Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Automatic Transfer Switch – Electrical Circuit, Operation, Video
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Electrical Basics > Automatic Transfer Switch – Electrical Circuit, Operation, Video

Automatic Transfer Switch – Electrical Circuit, Operation, Video

Learn how an Automatic Transfer Switch ensures continuous power by switching between main and generator supply lines.

Last updated: June 5, 2025 3:55 pm
K Mugunthan
Electrical Basics
No Comments
Share
7 Min Read
SHARE

In Today’s engineering world, it is an essential requirement for electrical devices to operate continuously without any disturbance, even though the main power is not available. For this instance only, we are using the Automatic Transfer Switch; this switch will continuously ensure the power to the system by automatically switching between the two power lines. One is the Main power supply line, and the second is the Generator Supply line.

Contents
Automatic Transfer Switch (ATS)SimulationComponentsCircuit DiagramOperation of Automatic Transfer SwitchConclusion

Automatic Transfer Switch (ATS)

The Automatic Transfer Switch does the job for a continuous power supply to the load by taking the power supply either from the Main Power line or the Generator Line. Usually, the load will operate in the Main Power Line only; if there is any fall or failure in the Main Power line means it will automatically take the supply from the generator line. In simple terms, any fault in the Main Line means the load will operate with the help of the Generator line. Once the fault is rectified means then the load will operate with the Main Power line automatically.

This system has minimum disturbances, and we can use it in many crucial applications of industrial plants. This system also ensures the safety of the connections through interlocks that prevent connections of both the main supply and generator line power source. The Major advantage of the system is uninterrupted power supply and is fully automatic, which will save time and process.

Simulation

Automatic Transfer Switch

Components

  1. 3-Pole Miniature Circuit Breaker (One for Power Line and One for Generator Line)
  2. 2-Pole Miniature Circuit Breaker (One for Power Line and One for Generator Line)
  3. Contactors (One for Power Line and One for Generator Line)
  4. Relay Coils
  5. On Delay Timer
  6. Contactor Coils
  7. Motor ( Electrical Load)

Circuit Diagram

Power Circuit:

automatic transfer switch working principle

Control Circuit:

how does automatic transfer switch work

Operation of Automatic Transfer Switch

Three-phase supply of 415 V from both the Power Supply Line and the Generator was given to the circuit. Both the supply lines were connected to the separate MCBs, the Power Supply Line was connected to 1 CB, and the Generator line was connected to 2 CBs.

automatic transfer switch for generator backup

Then both the MCBs were connected to the Contactor, which contacts the load, i.e., the Motor. 1 CB was connected to the contactor 1 (3 MCR), and 2 CB was connected to the contactor 2 (1 MCR).

While operating, both the MCBs 1 CB and 2 CB need to be in the ON condition for the automatic changeover. This completes the Main power circuit of the operation.

Single Phase supply of 230 V was given to the control circuit, likewise Power circuit in the control circuit also we are using two MCBs to control the contactor coils.

Power supply control line is directly connected to the two-pole circuit breaker 2CB, and the Generator line is directly connected to another two-pole circuit breaker 3CB.

The output of circuit breaker 3CB was directly connected to the relay coil 1 CR, timer coil 3CR, contactor coil 3 MCR, and its contacts.

Then the output of circuit breaker 4CB was directly connected to the relay coil 2 CR, contactor coil 1 MCR, and its contacts.

Power Supply of 415 V was given to the circuit breakers 1 CB and 2 CB, and both the MCBs were powered ON in the main circuit

Power Supply of 230 V was given to the circuit breakers 3 CB and 4 CB, and both the MCBs were powered ON in the control circuit.

Because of the power supply given to the circuit breaker, the 3 CB Relay coil 1CR got energized, which makes its contact close and energize the timer 3 CR. The contacts of the timer get closed after 2 2-second of delay.

automatic transfer switch in electrical systems

Once the timer contact gets closed, it will activate the contactor coil 3 MCR, which will make the contactor 3 MCR activate and which will energize the load, and the Motor will start rotating.

generator auto transfer switch function

At the same time, the Generator Line MCB 4CB also turned on, but the contactor coil will not get energized since the normally closed contact of Contactor 3 MCR was connected in series connection.

ATS switch with interlocking mechanism

Once the power is interrupted in the Power Supply line means the generator power will energize the contactor coil 1 MCR, and the motor rotates without stopping because of the continuous supply with the help of the backup generator supply. There will be no time gap or manual operation.

automatic changeover switch explained
smart automatic transfer switch design

Then, after the Power supply was rectified in the main line, the contactor 3 MCR will get activated and cut the supply to contactor 1 MCR, which means the load will work with the main power supply.

automatic load shifting between mains and generator
automatic transfer switch advantages

This was the working of this Automatic Transfer Switch, Load will primarily works with Main Power supply line and once the main power was interrupted means the load will work with Generator supply by automatic switch over and then after the clearance of interruptions then the main power supply will be connected automatically with few seconds of delay for smooth transition between the lines.

Conclusion

In this, we have discussed about the Automatic Transfer Switch connection in an Industrial appliance, which provides the uninterrupted power supply in an automatic manner by connecting the load to the power supply line and generator line based on the availability of power. This system is one of the important systems that continuously switch between the main power line and generator line with minimum disturbances. Its automatic function and safety operations make to use in many industries for their continuous operations and work.

Read Next:

  • Difference Between MCB and MCCB
  • What are Ground Faults and Earth Faults?
  • Difference Between MCB and RCBO
  • Control Two Motors in Sequence Circuit
  • Difference Between Earth and Neutral
  • Types of Tripping Protection in MCCB

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Transformer Testing – Routine Tests of Transformers
All About Electric Fence Gates
Understanding Protection Relays – 50, 50N, 51, 51N
Difference Between MCB and MCCB
Difference between Current Transformer and Potential Transformer
Top 100 Power Systems Projects – Electrical Engineering
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Difference between Stepper Motor and Servo Motor
What is an Electrical Drive? Types, Advantages, Disadvantages
What is an Armoured Cable? Classification of Cables
What is a Link Box?
Motor Protection Circuits
Difference Between Emergency STOP and Emergency Power OFF
PLC Panel and MCC Panel Interface Signals
What is a Soft Starter? Principle, Advantages, Disadvantages

Keep Learning

Ground Fault Versus Short Circuit

Difference Between Short Circuit and Ground Fault

Electrical Frequency

One Nation One Grid One Frequency – Electrical Engineering

Bonding and Grounding Electrical Systems

Testing and Inspection of Bonding and Grounding Systems

Capacitor Bank

What is a Capacitor Bank?

Difference Between Circuit Breaker and Fuse

Difference Between Circuit Breaker and Fuse

Effects of Long Distance Cables on VFD

Effects of Long Distance Cables between VFD and Motor

Motor Controls

Design and Implement Motor Control – Electrical Engineering

LCS Configuration equipped with LOTO Facility

Motor Control Signal Interface

Learn More

Two pressure transmitters

Pressure Transmitters Leg Compensation Technique

Programmable Logic Controller (PLC) Questions and Answers

Programmable Logic Controller (PLC) Questions and Answers – 6

Gyroscope Objective Questions

Gyroscope Objective Questions

Advances in Control System

Neural Networks

Power Electronics Objective Questions

Choppers Quiz

Mass Spectrometer Questions and Answers

Quadrupole Mass Spectrometer

How are Data Centers Cooled

How are Data Centers Cooled?

VFD Interview Questions and Answers

VFD Interview Questions and Answers – Electrical Drives

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?