Reading: What is Seal-in Circuit ?
Inst Tools > Blog > Animation > What is Seal-in Circuit ?
Last updated: March 4, 2021 4:33 pm
Animation PLC Tutorials
2 Comments
3 Min Read
A Seal-in circuit is a method of maintaining current flow after a momentary switch has been pressed and released.
What is Seal-in Circuit ?PLC Latching Animation
Seal in Circuit working
Fig 1 : Start button not pressed
Note : Consider a Relay is used to control the power supply to a motor. Here we are calling this relay as ” Motor Starter Coil “. This Relay another NO contact is used to seal-in or latch the start signal.
As start push button is a push & Release type i.e. signal will be available for some time say momentarily and then signal will be lost.
so we have to latch this circuit in order to make motor run continuously even after release of start push button.
For this purpose we are using Relay (M) NO contact across Start push button such that it will take care of start signal after start button is released.
The seal-in auxiliary contact (NO Contact) of the starter (M) is connected in parallel with the start button to keep the starter coil (M) energized when the start button released.
After Start Push button pressed : The Motor starter coil energized and its NO contact becomes NC as shown in below figure.
Seal-in Circuit
Fig 2 : Start button pressed
Start Button Not Pressed :
PLC Latching Circuit
Start Button Pressed & Released :
PLC Latching circuit Animation
During Starting, Start push button will give the signal to energize the coil (M), after that coil NO contact which is connected across
Start Push button will be used to latch the start signal as start push button will be released after pressing ( start button are momentary type ).
Also see : Relay Schematic Animation
  • Latched and Momentary Operation of Motor PLC Program
  • Push button Motor PLC Logic
  • Latches Objective Questions
  • PLC Automatic Control of Two Outputs with one Input
  • Solenoid Operated Valves and Latching Valves
SCADA Software and their Comparison
Potentiometer Working Principle Animation
What is Process Control?
Chemical Mixing Process using PLC
Down Counter PLC Program
2 Comments
  • Trojan says:
    February 17, 2022 at 4:07 pm
    Hi, there is wrong placement of the stop button. The relay will remain latched even when you press the stop button.
    • Jeremy Morissette says:
      November 26, 2023 at 11:33 pm
      I had the same thought
PLC Ladder Logic Example
User Defined Data Types (UDT) – Purpose, Need, Tutorial
Siemens PLC Organization Blocks (OB)
Automatic Motor Forward and Reverse Control using Timer
How to Add Unspecified CPU in Tia Portal?
Waste-Burning System OMRON PLC Program Example
Perfume filling system PLC program
CX Programmer Example: Perfume Mixing and Filling System
PLC Motor Logic with START, STOP, TEST Push buttons
How to Program Sequential Outputs in PLC
PLC Count values higher than 999
Structured Text PID control loop in PLC
Download Modscan software
How to Use ModScan Software for Testing Modbus Communication?
ControlLogix 5580 Controllers
Rockwell PLCs for Large Scale Applications
Causes of PLC Stop Mode
Various Causes for PLC Going in Stop Mode
Heat Recovery in HVAC System
IPv4 vs IPv6 - What’s the Difference Between IP addresses
IPv4 vs IPv6 – What’s the Difference Between IP addresses?
Insulators, Conductors and Semiconductors
Why Starting Current of Induction Motor is High
Bottle’s Capping with Rotating Mechanism
PLC FBD Program for Bottle’s Capping with Rotating Mechanism
Arc Fault Breaker (AFB) Electrical Problem Solved
Premature Arc Fault Breaker Failures
Instrument Control Package (ICP)
Package Control and Safety Systems Implementation Methods
Batch mixing process automation with Omron PLC
Automate Batch Mixing with Repeated Cycles in Omron PLC