A burner management system (BMS) monitors the status of the flame at the base of this incinerator, to ensure fuel gas does not keep entering the combustion chamber unless there is an established fire to burn it:
burner management system P&ID
Explain the purpose of solenoid valve SV-115, identifying whether it is normally energized (NE) or normally de-energized (NDE).
Also, explain the purposes of SV-111, SV-112, and SV-113 in this incinerator control system.
Answer :
Solenoid SV-115 vents all actuating air pressure from flow control valve FV-38 whenever its coil is de-energized.
Thus, SV-115 is “normally energized” to maintain actuating air pressure to FV-38.
Solenoids SV-111, SV-112, and SV-113 act to prevent fuel gas from reaching the incinerator’s burner assembly when the Burner Management System (BMS) sends a trip signal. SV-111 and SV-112 are block valves, while SV-113 is a bleed (“vent”) valve, making this a “double-block and bleed” valve arrangement.
A similar solenoid valve arrangement can be seen on the pilot burner gas line with solenoids SV-101, SV-102, and SV-103.
Read All SOV Questions & Answers
Solenoid Valves Questions & Answers – 2
Solenoid Valves Questions & Answers – 3
Solenoid Valves Questions & Answers – 4
Solenoid Valves Questions & Answers – 5
Solenoid Valves Questions & Answers – 6
Solenoid Valves Questions & Answers – 7
Differential Pressure Sensor with Pair of Strain Gauges
Programmable Logic Controller (PLC) Questions and Answers – 9
Problem on Weigh feeder
Calculate the appropriate millivoltage values of a Thermocouple
Compressor Emergency Shutdown Root Cause Analysis
Questions on Level Switches
Surface-mounted Water Pump
Electric-driven Air Compressor Troubleshooting
How Do You Connect the Differential Pressure Gauge at the Filter?
Identify Instrumentation Terms in Water Supply System
Simple High Level Indicator Circuit
DP Transmitter Error Calculations
Motor ladder Logic
Pitot tube
Pitot Tube Flowmeter Calculations
Suppose the lamp refuses to light up
Indentify Faults in Simple Lamp Circuit including Failed Wires
displacer level transmitter configuration
Displacer Level Transmitter Questions
Programmable Logic Controller (PLC) Questions and Answers – 7
Electronic Force Balance Pressure Transmitter
Process Switches Normal Status
Calculate Hydrostatic Pressure of a vertical column of Acetic Acid
Electrical Contactor, Switch, Circuit Breaker
Difference between Solid Conductor and Stranded Conductor
Pressure Gauges with Diaphragm Sensor Principle
Fluorescent Screen of CRT
CRT Fluorescent Screen
Diesel Engine Fire Hydrant Pump
Fire Fighting System
Capacitive Transducers Objective Questions
Control Speed of an Induction Motor using Analog Output of PLC
Control Speed of Induction Motor using Analog Output of PLC
Light Tower in Industrial Automation
PLC Examples for calling functions in SCL