Reading: Scaling with Parameters (SCP) Instruction in PLC
Inst Tools > Blog > PLC Tutorials > Scaling with Parameters (SCP) Instruction in PLC
Last updated: March 4, 2021 3:24 pm
6 Comments
To study the working of Scaling with Parameters (SCP) Instruction in Allen Bradley programmable logic controllers (PLC).
Scaling with Parameters (SCP) InstructionBlock Name: SCP – Scaling with parametersFunction of SCP :Program Logic :PLC Program :Example PLC Logic with SCP InstructionWhen Level Transmitter gives 0 mA (N7:1)When Level Transmitter gives 7 mA (N7:1)When Level Transmitter gives 18 mA (N7:1)When Level Transmitter gives 20 mA (N7:1)Conclusion:
Scaling with SCP Instruction
In the above picture, there are totally six parameter ,
Input
Integer Value address-From Field instrument which is to be scaled
Input Minimum
Minimum Input value (Ex: 4 to 20 mA from level transmitter means 4 mA is the input minimum value)
Input Maximum
Maximum Input value (Ex: 4 to 20 mA from level transmitter means 20 mA is the input maximum value)
Scaled Minimum
Minimum scale value (0 to 32767 is the maximum positive acceptable number in AB PLC-Minimum Scaled value is 0)
Scaled Maximum
Maximum scale value (0 to 32767 is the maximum positive acceptable number in AB PLC-Maximum Scaled value is 32767).
Function of SCP :
The Input value is scaled to a range determined by creating a linear relationship between input min and max values and scaled min and max values. The scaled result is returned to the address indicated by the output parameter.
Parameters may be integer, long, floating-point or immediate data values or addresses containing values. The Input value is scaled to a range determined by creating a linear relationship between input min and max values and scaled min and max values.
Program Logic :
Let s study the working with simple example,
Get the level of the water from level transmitter (4 to 20mA),
Give the notification
If level transmitter become faulty,
If level transmitter range between 4 to 8 mA, give the notification as water level low
If level transmitter range between 16 to 20 mA, give the notification as water level high.
If level transmitter reaches 20mA, give the notification to stop motor.
PLC Program :
Push button Latched with Memory
Rung 0000 :
Start/Stop  PB latched with memory.
Rung 0001 :
When Start is pressed move the value stored in N7:0 to N7:1
Scaling Block (SCP) in PLC
Rung 0002 :
Scaling block is used to scale the input to PLC value.(4mA -0 /20mA-32767)
Rung 0003 :
Level transmitter is configured to give 4mA when tank level is zero, if transmitter gives 0 instead of 4mA it means transmitter is faulty. Comparator block is used to compare and give notification to any one of the digital output like lamp.
Limit Block in PLC
Rung 0004 :
Limit block is used to range the values between 4 to 8mA, and give the notification as water level is low.
Rung 0005 :
Limit block is used to range the values between 16mA to 20mA, and give the notification as water level is high.
Comparator Block in PLC
Rung 0006 :
Comparator block is used to compare the high end value and give the notification to turn stop motor.
Scaling Example in PLC
Level Transmitter configuration in PLC
Scale with Parameters (SCP) Instruction
Limit Instruction in Ladder Logic
Working Scaling block in AB PLC
Allen Bradley Scaling Logic
Conclusion:
We can use this example to understand the working scaling block in AB PLC.
Author : Hema Sundaresan
Single Push button Ladder Logic
Motor Logic with Push buttons
What is Latching in PLC ?
Masked Move Instruction in PLC
What is Interlocking in PLC ?
Turbine-Compressor System Architecture
Establishing a Modbus Driver for SCADA Indusoft Web Studio
Siemens PLC Interview Questions and Answers
FB Block in Siemens PLC Programming
6 Comments
  • Jairo Francisco Oliveira Paula says:
    August 12, 2019 at 5:39 am
    the SPC function is an advanced level instruction in programming .. I would like posts to turn signal 4 to 20 mA through that instruction
    March 2, 2020 at 8:59 am
    NO RETURN TO MY QUESTION. I FOLLOW THIS PAGE FOR A LONG TIME.
    March 2, 2020 at 9:01 am
    Hema Sundaresan CAN ANSWER ME PLEASE!
  • Hemalatha Sundaresan says:
    March 2, 2020 at 9:54 am
    Hello Jairo Francisco,
    I am really sorry for the late response.
    That part will be in output scaling part,where you can turn 32767 to 20mA and 0 to 4 mA.
    March 29, 2020 at 10:24 pm
    Thank you very much Hemalatha Sundaresan !! you could create more examples that work with signal 4 to 20 ma using the AB PLC.
    I am using this example on a temperature transmitter.cc
  • Jone says:
    February 12, 2022 at 9:14 pm
    How I can implement level control in VBA excel?
How to Configure PID Controller in Various Schneider PLCs?
Mitsubishi Electric GOC Controllers
What is a Annunciator Panel?
Basic Pumping System Application Used in Industrial Automation
Communication between Factory IO and Siemens Tia Portal
Programmable Logic Controller Questions and Answers
PLC SCL Program for Marking Machine
PLC Programming Example on Timers Function Block
Profibus DP Master
DP Master System Configuration in PLC
Parameters of SRT_DINT instruction
Tia Portal – OB20 Time Delay Interrupt Organization Block
Wiring in PLC System
Wiring in a PLC Control Panel
Ladder Logic Programming Examples
Difference Between PNP and NPN Sensors
Relay Symbols
Relay circuits
PLC Program for Automatic Door Control System
PLC Automatic Door Control System – Programming Example
Things to Know When Measuring Voltage
Relay ladder diagram example
How to Draw a Schematic Diagram ?
Difference between Transparent Level Gauge and Reflex Level Gauge
Marking Polarity
Geothermal Air Conditioners
Types of Air Conditioning Systems
How to Select a SCADA for New Project
How to Select a SCADA for New PLC Project?
Interview Questions on Industrial Wireless