Reading: 100 Electrical Circuit Breaker Quiz
Inst Tools > Blog > PLC Tutorials > 100 Electrical Circuit Breaker Quiz
Test your knowledge with the 100 quiz questions and answers on the electrical circuit breaker, generators, and electrical equipment.
Last updated: January 9, 2022 10:24 am
PLC Tutorials Electrical MCQ
9 Min Read
Image Courtesy: Pixabay
The below mentioned the sample 15 questions from the quiz.
Question 1:
When a typical 4,160 volt breaker is racked to the TEST position, control power is __________ the breaker; and the breaker is __________ the load.
A) removed from; connected to
B) available to; connected to
C) removed from; isolated from
D) available to; isolated from
Question 2:
While remotely investigating the condition of a normally-open 480 VAC motor control center (MCC) feeder breaker, an operator observes the following indications:
Green breaker position indicating light is out.
Red breaker position indicating light is lit.
MCC voltmeter indicates 480 VAC.
MCC ammeter indicates zero amperes.
Based on these indications, the operator should report that the feeder breaker is __________ and racked __________.
A) open; in
B) open; to an unknown position
C) closed; in
D) closed; to an unknown position
Question 3:
Which one of the following evolutions will draw the highest current from the main generator during operation of the output breaker?
A) Closing the output breaker with voltages out of phase
B) Opening the output breaker under no-load conditions
C) Closing the output breaker with voltages in phase
D) Opening the output breaker under full-load conditions
Question 4:
If a breaker is racked to the TEST position, the
A) breaker can only be operated remotely from its associated remote control panel.
B) normal breaker opening and closing operations cannot be tested because the TEST position is for overload testing only.
C) electrical jumpers must be connected to the operating coils to operate the breaker.
D) remote position indication for the breaker is still operational
Question 5:
Which one of the following results from a loss of control power to a breaker supplying a motor?
A) The breaker position will remotely indicate closed regardless of actual position.
B) The breaker will trip open due to the actuation of its protective trip device.
C) The motor ammeter indication will be zero regardless of actual breaker position.
D) The charging motor will not recharge the closing spring after the breaker closes.
Question 6:
A main generator is being connected to an infinite power grid that is operating at 60 Hz.
Generator output voltage is equal to the grid voltage but generator frequency is at 57 Hz.
Which one of the following generator conditions is most likely to occur if the generator output breaker is closed with voltages in phase (synchronized), but with the existing frequency difference?
(Assume no generator breaker protective trip occurs.)
A) Underfrequency
B) Overspeed
C) Reverse power
D) Undervoltage
Question 7:
Loss of breaker control power will cause
A) the remote breaker position to indicate open regardless of actual breaker position.
B) inability to operate the breaker locally and remotely.
C) failure of the closing spring to charge following local closing of the breaker
D) breaker line voltage to indicate zero regardless of actual breaker position.
Question 8:
A typical 120 VAC manual circuit breaker tripped due to overload.
To close this circuit breaker, the handle must be moved from the
A) midposition directly to the ON position; trip latch reset is not required.
B) OFF position to the midposition to reset the trip latch, and then to the ON position
C) midposition to the OFF position to reset the trip latch, and then to the ON position.
D) OFF position directly to the ON position; trip latch reset is not required
Question 9:
Which one of the following will provide the first motor protection against electrical damage caused by gradual bearing degradation?
A) Overcurrent trip relay
B) Thermal overload device
C) Undervoltage device
D) Underfrequency relay
Question 10:
Breaker local overcurrent trip flag indicators, when actuated, indicate that
A) a breaker overcurrent condition is responsible for a breaker trip.
B) a breaker trip will occur unless current is reduced.
C) the associated breaker has failed to trip open during an overcurrent condition
D) an overcurrent condition has cleared and the breaker can be closed.
Question 11:
A diesel generator (DG) was initially operating at 80 percent of rated load supplying an isolated electrical bus when a malfunction caused the DG output breaker to trip.
The breakers for all of the bus loads-all of which are large motors remained closed, preparing the motors to restart upon restoration of power to the bus.
The DG output breaker has been repaired.
With all of the bus load breakers still closed, which one of the following will occur when the DG output breaker is closed to reenergize the bus?
A) The DG will experience severe overload conditions.
B) The DG will return directly to its initial load.
C) The DG will experience slight overload conditions.
D) The DG will become lightly loaded.
Question 12:
A 480 VAC motor control center supplies a load through a breaker and a manual disconnect switch.
Which one of the following sequences will provide the greatest level of personnel safety when de-energizing the load for maintenance, and when re-energizing the load after the maintenance is complete?
A) DE-ENERGIZING – Open disconnect switch first, RE-ENERGIZING – Shut breaker first
B) DE-ENERGIZING – Open breaker first, RE-ENERGIZING – Shut disconnect switch first
C) DE-ENERGIZING – Open disconnect switch first, RE-ENERGIZING – Shut disconnect switch first
D) DE-ENERGIZING – Open breaker first, RE-ENERGIZING – Shut breaker first
Question 13:
A thermal overload device for a large motor protects the motor from.
A) sustained overcurrent by opening the motor breaker or motor line contacts
B) sustained overcurrent by opening contacts in the motor windings.
C) instantaneous overcurrent by opening the motor breaker or motor line contacts.
D) instantaneous overcurrent by opening contacts in the motor windings
Question 14:
During a routine inspection of a main generator output breaker, a technician discovers severely damaged main contact surfaces.
Which one of the following is the most likely cause of the damaged contact surfaces?
A) The main generator breaker automatically tripped open due to a faulty trip relay actuation while the main generator was operating unloaded.
B) The main generator breaker automatically tripped open after it was closed with the generator and power grid voltages 60 degrees out of phase.
C) The main generator breaker automatically tripped open after it was closed with the generator and power grid voltages in phase but with generator frequency 0.2 Hz lower than power grid frequency.
D) The main generator breaker automatically tripped open on a loss of offsite power while the main generator was operating at its maximum rated load.
Question 15:
Which one of the following generator conditions is most likely to result in equipment damage from high current flow?
A) Tripping the generator prime mover under full-load conditions.
B) Closing the output breaker onto a bus that has a short-circuit fault.
C) Tripping the output breaker under full-load conditions.
D) Closing the output breaker onto a bus that has an open-circuit fault.
All 100 questions and answers are available in the Quiz.
Instrumentation Quiz
Engineering MCQ:
  • Control System MCQ
  • Electrical Engineering MCQ
Procedure for Siemens S7-300 Download from PC to PLC
What is Relay Logic ?
User Defined Data Types (UDT) – Purpose, Need, Tutorial
What is Seal-in Circuit ?
What are Trends in SCADA?
Synchronous Motors Power and Torque Questions
Components of SCADA
How to Troubleshoot Siemens PLC Programs?
Transferring Data Across PLC Systems – TSEND_C and TRCV_C
Synchronous Machine Multiple Choice Questions
Parking Garage Indicator: PLC Automation System
Turbine-Compressor System Architecture
What is Contextual HMI? – HMI Screens on a Mobile or Tablet
Database in Siemens PLC
Steps to Configure TCP/IP Communication in Siemens S7-1200 PLC
Circuit Control Devices Multiple Choice Questions
Circuit Control Devices Multiple Choice Questions & Answers
PLC Program for Valves
PLC Pump Permissive Interlocks
PLC and MCC Panel Interface Design
Electrical Machines MCQ Series 16
Schneider Electric Modicon M340 PAC
PLC vs PAC – Understanding the Key Differences and Similarities
Electricity and Magnetism Questions & Answers
Top 300 Electricity and Magnetism Questions & Answers
PLC-Complete-Training-Package
Free PLC Training Software Download
Synchronous Generator Salient Pole vs Non Salient Pole
Phosphate Dozing System
Phosphate Dozing System Problems
Stability in Frequency Domain
Tuning of PID Controllers
Pre-Startup Safety Review (PSSR)
Instrument Calibration Questions
Inter Discipline Check (IDC)
What is Inter Discipline Check (IDC)?
PLC Ladder Logic Example based on Set Coil and Reset Coil
Car Cooling System Automotive Radiator
What is an Automotive Radiator?