Reading: Resistance Temperature Detector (RTD) Questions – 1
Inst Tools > Blog > Practical Questions > Resistance Temperature Detector (RTD) Questions – 1
Last updated: June 6, 2018 9:49 am
Practical Questions
1 Min Read
Calculate Temperature from the RTD
Question :
Suppose you need to determine the temperature of a fluid inside a pipe. Installed in this pipe is a 2-wire 100 Ω RTD inside a thermowell, not connected to a transmitter or any other circuit. You happen to have a multimeter with you to measure resistance at the RTD leads.
Touching the two test leads of your multimeter together, you measure 0.3 Ω. Then, connecting those same leads to the RTD’s wires, you measure 184.6 Ω. You do not happen to have an RTD table with you, but you do carry a calculator.
Calculate the approximate temperature of the fluid in this pipe, assuming the most common α value for 100 Ω RTDs.
Answer :
The α value is most likely 0.00385, resulting in a calculated temperature of 218.96 oC or 426.13 oF.
Flapper Nozzle Questions
Is it Possible to Measure Liquid-Liquid Level Interface using Float?
How Manometer Measures Differential Pressure for Different Fluids?
Loop Powered Pressure Transmitter
pH Transmitter Problem
Questions on Pressure Transmitter Calibration Setup
Upgrading the Electrical System in an Automobile
Displacer Level Transmitter Question & Answer
Practical Process Control System Questions & Answers – 7
Electronic Pressure Sensor with Bourdon Tube and LVDT
Paint Mixing System
Motor Trip Logic using PLC Programming
Programmable Logic Controller (PLC) Questions and Answers – 14
Programmable Logic Controller (PLC) Questions and Answers – 15
Practical Control Systems Questions & Answers
Practical Process Control System Questions & Answers – 3
steam heat exchanger
Practical Process Control System Questions & Answers – 9
Guided-wave Radar Asset Management Parameters
Which instrument is faulty
Which Instrument is Faulty? Transmitter, Recorder, or Controller
Process Control Loop Testing
compressor emergency shutdown system
Compressor Emergency Shutdown Root Cause Analysis
process conditions, Find out the Circuit Components Status
As per Process Conditions, Find out the Circuit Components Status ?
Single-Phase Full Wave AC-DC Converter Questions
How to Test a Transistor using Multimeter
Relay Parts
NO vs NC Contact
Instrument Air Calculations
Basic Calculations of Instrument Air
Swiss Screw Machining
Things You Should Know About Swiss Screw Machining
Safety Instrumented System (SIS) Worksheets
Safety Instrumented System (SIS) Worksheets and Documents
Normally closed input actuator as stop button.
Normally-Closed Contacts for Stop Buttons
Types of Equipment Needed to Run a Successful Auto Repair Shop