Write the PLC program to control multiple pumps using programmable logic controllers. We have two input pumps used to fill a tank. Make sure pumps operate in an equal amount of time over their lifetime.
Multiple Pumps Control using PLC
![Multiple Pumps Control using PLC Multiple Pumps Control using PLC](https://instrumentationtools.com/wp-content/uploads/2019/11/Multiple-Pumps-Control-using-PLC.jpg)
Program Logic:
Develop ladder logic program according to the logic given below,
- The start/stop push button is provided for control of the two input pump motors P1 and P2.
- The Start/Stop pushbutton station is operated to control pump P1.
- When the tank is full drain pump motor P3 is started automatically and runs until the low-level sensor is actuated.
- After 3 fillings of the tank by pump P1 control automatically shifts to pump P2.
- The operation of the start/stop pushbutton now controls pump P2.
- After 3 fillings of the tank by pump P2, the sequence is repeated.
PLC Program:
![PLC based Multi-Pump Logic PLC based Multi-Pump Logic](https://instrumentationtools.com/wp-content/uploads/2019/11/PLC-based-Multi-Pump-Logic.jpg)
![Pump Control with a PLC Pump Control with a PLC](https://instrumentationtools.com/wp-content/uploads/2019/11/Pump-Control-with-a-PLC.jpg)
Program Description:
Rung 0000:
Start/Stop PB latched with memory B3:0/0.
Rung 0001:
B3:0/0 enabled to turn on B3:0/1 which is to turn ON PUMP P1 (O:0/0) when low-level sensor(I:0/3) turn ON and High-level sensor (I:0/2) is in off condition.B3:0/1 is latched with low-level sensor because pump p1 should not go off once water started rising.
Rung 0002:
Memory contacts used to turn on PUMP P1 (O: 0/0) with counter (C5:0).
Since we are going to shift pump operation from P1 to P2, two counters are used to shift between Pl and P2.
Counter C5:1 is used to turn on PUMP P2(O:0/2).
Rung 0003 & 0004:
B3:0/0 enabled to turn on B3:0/2 which is to turn on PUMP P3(O:0/1) when high-level sensor(I:0/2) turn ON and low-level sensor (I:0/3) is in off condition.B3:0/2 is latched with high-level sensor because pump p3 should not go off once water started reducing.
Rung 0005:
When Pump 3 (O: 0/1) is running, the low-level sensor turns on will make Pump p3 off and pump P1(O:0/0) ON.
Rung 0006:
Both Counter reset is done once the second counter (C5:1) done bit turns ON.
Conclusion:
We can use this example to understand the programming logic in AB PLC.
Author: Hema Sundaresan
- PLC Example with Timers
- Traffic Light Control using PLC
- One-Shot Rising Instruction in PLC
- Count Running Hours of Pumps
- Communication between PLC & Energy Meter