The following empirically derived thermocouple laws, are useful to understand, diagnose and utilise thermocouples.
a) Law of homogeneous circuits
If two thermocouple junctions are at T1 and T2, then the thermal emf generated is independent and unaffected by any temperature distribution along the wires.
In above Figure, a thermocouple is shown with junction temperatures at T1 and T2. Along the thermocouple wires, the temperature is T3 and T4. The thermocouple emf is, however, still a function of only the temperature gradient T2 – T1.
b) Law of intermediate metals
The law of intermediate metals states that a third metal may be inserted into a thermocouple system without affecting the emf generated, if, and only if, the junctions with the third metal are kept at the same temperature.
Law of intermediate metals Principle
When thermocouples are used, it is usually necessary to introduce additional metals into the circuit This happens when an instrument is used to measure the emf, and when the junction is soldered or welded. It would seem that the introduction of other metals would modify the emf developed by the thermocouple and destroy its calibration. However, the law of intermediate metals states that the introduction of a third metal into the circuit will have no effect upon the emf generated so long as the junctions of the third metal are at the same temperature, as shown in Above Figure
c) Law of intermediate temperatures
The law of intermediate temperatures states that the sum of the emf developed by a thermocouple with its junctions at temperatures T1 and T2, and with its junctions at temperatures T2 and T3, will be the same as the emf developed if the thermocouple junctions are at temperatures T1 and T3.
Law of intermediate temperatures Principle
This law, illustrated in above Figure, is useful in practice because it helps in giving a suitable correction in case a reference junction temperature other than 0 °C is employed. For example, if a thermocouple is calibrated for a reference junction temperature of 0 °C and used with a junction temperature of 20 °C, then the correction required for the observation would be the emf produced by the thermocouple between 0 °C and 20 °C.
Also Read: RTD or Thermocouple ?
What to Choose RTD or Thermocouple ?
How to Select Right Thermocouple & Thermowell ?
What is RTD Sensitivity ?
What is a Probe Thermometer? How to Calibrate and Use it?
Difficulties with Thermocouples for Temperature Measurement
Thermowell Outer Diameter Larger than Nozzle Inside Diameter?
What is a Head Mount Temperature Transmitter? – Advantages
Effect of Lead Wire Resistance on RTD
What is a Thermopile ?
Liquid In Glass Thermometer Principle
RTD Sensor Connections
What is a Three-wire RTD ?
How Does an Infrared Thermometer Work
How Does an Infrared Thermometer Work?
bimetallic thermometer working principle
Different Types of Thermometers
testing-thermocouples-and-rtds
Testing thermocouples and RTDs using Multi-function Calibrators
Insulation of Thermowell
Facts on Thermowell Insulation Thickness
calibrating-and-testing-rtd-sensors
RTD Calibration Procedure
PTC NTC Thermistors Comparation
Thermistor Working Principle
RTD lead resistances Wiring
Resistance Temperature Detectors Working Principle
Filled-bulb Temperature Measurement
Filled-bulb Temperature Sensors
mass spectrometer sample system
Mass Spectrometer Working Principle
Quiz on Alternators, Motors, and Transformers
200+ Quiz on Alternators, Motors, and Transformers
Batteries Connected in Parallel
Battery Operation : Series and Parallel
Crowbar fault protection circuit
pressure gauge snubber
Pressure Gauge Snubbers
Difference Between CNC Machine and VMC Machine
Gas-detection-system
Selection Criteria for Toxic Gas Detector
Dynamic Braking Resistor in VFD