The following storage vessel holds liquid heptane, a hydrocarbon with an approximate specific gravity of 0.68.
A pressure transmitter located at the bottom infers heptane level by hydrostatic pressure (head).
Determine the calibration range of this pressure transmitter in order to properly translate the range of vessel level (0 to 14 feet) into an output signal of 4 to 20 mA.
Transmitter Calibration Range
Then, determine the following (assuming the transmitter has been properly calibrated for the application):
Transmitter output signal (mA) at 8 feet of level
Heptane level at 5.7 mA signal output
Answer
Lower range-values (LRV): 0 inches W.C. input = 4 mA output
Upper range-values (URV): 114.24 inches W.C. input = 20 mA output
Transmitter output signal (mA) at 8 feet of level = 13.14 mA
Heptane level at 5.7 mA signal output = 1.4875 feet
Share your answers & explanation with us through the below comments section.
- Impulse Tubing Leak
- Control Valve Noise
- Density and Specific Gravity
- Pressure Sensing Level Sensor
- LRV URV of DP Level Transmitter
Credits: Tony R. Kuphaldt