Reading: Pneumatic Level Transmitter Value Struck?
Inst Tools > Blog > Practical Questions > Pneumatic Level Transmitter Value Struck?
Pneumatic level transmitter is stuck at one measurement value of approximately 40% even when the process liquid level rises and falls.
Last updated: January 12, 2021 6:48 pm
Practical Questions
2 Min Read
Suppose a level measurement system is “stuck” at one measurement value of approximately 40% even when the process liquid level rises and falls between 20% and 80% of range (as indicated by the sight-glass):
Note: Pneumatic level transmitters were obsolete and no more found in industries.
An instrument technician removes the cover from the pneumatic transmitter and momentarily presses the baffle against the nozzle. The level indicator in the control room does not respond at all but remains fixed at about 40%.
Identify the likelihood of each possible fault in this list shown in the below table – whether the fault is “probable” (worth considering as a cause of this system’s trouble) or is “unlikely” (either completely ruled out as a cause, or just not worth considering at this point in the diagnosis) – following the results of the technician’s test:
Identify the below list of faults probable or unlikely to occur.
  1. Plugged isolation valve
  2. Plugged equalizing valve
  3. Fill fluid lost in “wet” leg
  4. Low supply air pressure
  5. Transmitter restrictor (orifice) clogged
  6. Indicator pointer stuck
  7. Transmitter nozzle clogged
  8. 3-15 PSI signal tubing plugged
  9. Transmitter out of calibration
Share your answers and explanation with us through the below comments section.
  • Level Instrument Faulty
  • Types of Level Measurement
  • Troubleshooting Current Loops
  • Lead Wire Resistance on RTD
  • Radar Incident Power
Credits: Tony R. Kuphaldt
Practical Level Sensors Questions and Answers
Why Strain Gauge Resistance Changes as it Stretches and Shrinks?
Define Normal Status of a Process Switch ?
What is the Simple Alternative Vessel Level Indication?
Solenoid Valves Questions & Answers – 2
Compressor Emergency Shutdown Root Cause Analysis
Identify the Problem in the PLC Program
Analytical Process Control Question
Identify Solenoid Valves Energized or de-energized?
Programmable Logic Controller (PLC) Questions and Answers – 11
Pressure Transmitter Re-Range Questions
Investigate High Level Alarm of Distillation Process
Paint Mixing System
Solenoid Valves Questions & Answers – 3
Calibration setup for a low-range electronic pressure transmitter
Instrument Lab Exercise – Ranging and Manometer Usage
Simple High Level Indicator Circuit
Loop Diagram
PT Loop Diagram Faults
Analytical Control System of Heat Exchanger Questions
Problem on Solar Hot Air Collector and Variable Speed Fan
Two Differential Pressure Transmitters
Pressure Level Transmitter Problems
Baffle Nozzle Question
ORP-sensor-calibration
Oxidation-Reduction Potential (ORP) Sensor Calibration Procedure
Fundamental Motion Control Commands
Cage-guided globe valves
What is Cage-guided Globe Valve ?
Temperature Sensors Questions
Questions on Thermocouple and Pyrometer
Level Gauge Interface Measurement
Level Gauge Interface & Temperature Problems
Optimal Control Systems
Output Regulator & the Tracking Problem
Valve Face to Face Dimension
Face to Face Dimension of Control Valve
Things to Know When Measuring Voltage