Reading: Investigate High Level Alarm of Distillation Process
Inst Tools > Blog > Practical Questions > Investigate High Level Alarm of Distillation Process
Suppose the operator of this distillation process calls you to investigate a high-level alarm he is receiving on LAH-58.
Last updated: November 16, 2020 6:49 pm
Practical Questions
2 Min Read
Operator doesn’t think this should be happening, because LIC-38 registers a liquid level of 5’-1” in the bottom of the tower, which is a bit less than setpoint (5’-4”).
Your first test is to measure the current signal from LT-38a, and you find that to be 10.67 mA (LT-38a is ranged 3’-0” to 8’-0”):
Identify which faults could account for this problem. Find out the below mentioned problems are possible or impossible?
  • LSH-58 failed
  • LAH-58 failed
  • LSL-57 failed
  • LAL-57 failed
  • LT-38a calibration error
  • LIC-38 (input) calibration error
  • FIC-37 (input) calibration error
Answer
It is highly unlikely that LT-38a is at fault because the controller (LIC-38) receives the median-selected signal from three different level transmitters.
In order for the 10.67 mA signal to be incorrect, at least one of the other two level transmitters (LT-38b or LT-38c) would also have to be experiencing the same calibration error! In other words, this scenario would require coincidental faults, which are highly unlikely.
The below list shows the possible and impossible scenarios.
  • LSH-58 failed – Possible
  • LAH-58 failed – Possible
  • LSL-57 failed – Impossible
  • LAL-57 failed – Impossible
  • LT-38a calibration error – Impossible
  • LIC-38 (input) calibration error – Impossible
  • FIC-37 (input) calibration error – Impossible
Share your answers and explanation with us through the below comments section.
  • Purge Level Transmitter
  • PLC Alarm Acknowledge
  • Vessel Calibration Range
  • Total Hydrostatic Pressure
  • Valve Flow Direction
Credits: Tony R. Kuphaldt
Vertical Tube Liquid Level Equilibrium
Practical Process Control System Questions & Answers – 7
How Manometer Measures Differential Pressure for Different Fluids?
Programmable Logic Controller (PLC) Questions and Answers – 8
Fisher model 546 I/P transducer
Questions on DP Transmitter Wet Leg Compensating Impulse Line
Pneumatic Relay Questions
How to Connect Proximity Switch (Sink Type) to Make LED ON ?
Upgrading the Electrical System in an Automobile
Sketch a Ladder Diagram for PLC to Energize the Lamp
Paint Mixing System
Is it Possible to Measure Liquid-Liquid Level Interface using Float?
Calculate Amount of Weight Indicated by the Scale
Identify Instrumentation Terms in Water Supply System
Which instrument is faulty
Which Instrument is Faulty? Transmitter, Recorder, or Controller
Allen-Bradley MicroLogix controller
Programmable Logic Controller (PLC) Questions and Answers – 15
Identify which lamp in the following ladder-logic diagram
Identify High Flow Alarm and Low Flow Alarm?
Determine Level of Liquid in the Vessel and its Specific Gravity
Siemens PLC Block Diagram
Programmable Logic Controller (PLC) Questions and Answers – 14
Overhead Product Pressure Control Loop
Thermocouple Questions
Thermocouple Terminal block Questions
thermocouple Transmitter Formula
Calculate Process Temperature using a Thermocouple
Benefits of Pursuing a Degree in Engineering
Solenoid Valve Failure in Plant Start-Up
Control Methods in Servo Motor Drives
Various Control Methods in Servo Motor Drives
Nuclear Magnetic Resonance Spectrometer Questions & Answers
Electrical Machines MCQ Series 7
Wedge Flow Meter
Wedge Flow Meter Principle
Weinview HMI
Thermocouple Temperature Measurements Errors
Thermocouple Temperature Measurement Errors