Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Ammonia Gas Detector Working Principle and Calibration
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Analyzers > Ammonia Gas Detector Working Principle and Calibration

Ammonia Gas Detector Working Principle and Calibration

Last updated: July 20, 2019 11:26 am
Editorial Staff
Analyzers Calibration
No Comments
Share
5 Min Read
SHARE

Ammonia gas detector working principle and calibration. (Make: Dragger Model : Polytron 5100)

Gas detector is a very important safety device for any chemical plant. Its can give information in any small leak from any pipelines and with early action we can save any incident in plant.

In any chemical plant generally we use four types detector:

  1. Hydrocarbon Detector
  2. CO detector
  3. NH3 detector
  4. Chlorine detector

Here we discussed about Ammonia detector.

Principle :

Ammonia detector works on electrochemical principle. Electrochemical sensors are electrochemical measuring transducers for measuring the partial pressure of gases under atmospheric conditions. The ambient air being monitored diffuses through a membrane into the liquid electrolyte in the sensor. The electrolyte contains a measuring electrode, a counter-electrode and a reference electrode. An electronic potentiostatic circuit ensures a constant electrical voltage between the measuring electrode and reference electrode.

Voltage, electrolyte and electrode material are selected to suit the gas being monitored so that it is transformed electrochemically on the measuring electrode and a current flows through the sensor. This current is proportional to the gas concentration. At the same time, oxygen from the ambient air reacts at the counter-electrode electrochemically. The current flowing through the sensor is amplified electronically, digitized and corrected for several parameters (e.g. the ambient temperature). The resulting measured value is given as an analog, 4-20 mA signal.

Gas Detector Internal Circuit

Gas Detector Parts :

  1. Meter
  2. Potentiostat
  3. Direct current supply
  4. Measured gas
  5. Membrane
  6. Measuring electrode
  7. Electrolyte
  8. Reference electrode
  9. Counter electrode
  10. Temperature sensor

Configuration of Gas Detector:

Gas detector can be used as a two wire or as three wire device.

Connect the gas detector wiring as per your requirement & Power ON the detector. Display shows a start up timer.

Wait for the timer to complete and then press down navigation and go to FSD for Span range.

Ammonia Gas Detector Calibration

Calibration of Gas Detector:

For calibration we use N2 gas for zero calibration and 90 PPM ammonia cylinder for span gas .

Typical Calibration Setup : 

Gas Detector Calibration Setup

Parts :

  1. Regulator
  2. Calibration gas cylinders ( Zero Gas Cylinder & Span Gas Cylinder  )
  3. Calibration adapter

For zero calibration

  1. Connect the regulator with N2 cylinder adapter to detector then adjust the flow to 0.5 l/min
  2. Press down navigation key for 5 sec its showing -0- Adj.
  3. Tap [OK].
  4. The display will show the current value blinking.
  5. Wait for the value to stabilize.
  6. Use [UP] / [DOWN] navigation to adjust the value to 0.
  7. Enter [OK] then detector return to main menu.
  8. Turn off gas flow and remove the calibration adapter from the sensor or disconnect tubing.

Note : Ambient air can be used to zero the sensor instead of nitrogen or Zero Air if the area is known to be free of the target gas or any gas to which the sensor may be cross-sensitive. In this case, no cylinder or calibration adapter is needed for the zero calibration.

For span calibration

  1. Connect the regulator with 90 PPM ammonia cylinder adapter to detector then adjust the flow to 0.5 l/min
  2. Press down navigation key for 5 sec its showing -0- Adj. press down its showing SPn Adj
  3. Tap [OK].
  4. The display will show the current value blinking.
  5. Wait for the value to stabilize.
  6. Use [UP] / [DOWN] navigation to adjust the value (As mention on cylinder certificate, means span cylinder gas concentration).
  7. Enter [OK] then detector return to main menu.
  8. Turn off gas flow and remove the calibration adapter from the sensor or disconnect tubing.

General Preventive Maintenance : In every 6 months once, carry out the calibration of gas detector.

Reference : Drager Manual

Article by :
Ashish Agrawal
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Functional Testing of Control Valve Positioners
Dissolved Oxygen Analyzer Working Principle
Multiphase Flow Meter Calibration Procedure
Important Terms in Calibration
What is a Dead Weight Tester?
Self Actuated Pressure Control Valve Functional Testing
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Online Gas Chromatograph Principle
Conductivity Analyzer Common Problems and Troubleshooting Tips
Methods of Measurement
Basics of Suspended Particulate Matter (SPM) Analyzers
Differential Pressure Switch Calibration Procedure
Tunable Diode Laser Analyzer Working Principle
Differential Pressure Sensors Calibration Procedure
Hybrid Level Measurement Principle, Selection, Installation, Limitations and Calibration

Keep Learning

Open-Tank-DP-Level-Transmitter-with-Zero-Suppression-Calibration

DP Level Transmitter with Zero Suppression Calibration

Calibrate Eddy Current Conductivity Instrument

How to Calibrate the Eddy Current Conductivity Meter?

Temperature Switch Calibration

How to Calibrate Temperature Switch? – Instrument Basics

Pig Signalling Switches Functional Testing

Pig Signalling Switches Functional Testing

Sling Psychrometer Principle

Sling Psychrometer Principle

Stroke Checking Procedure for GCV, SRV, IGV, and LFBV

Stroke Checking Procedure for GCV, SRV, IGV, and LFBV

4-wire pH Transmitter Problem

pH Transmitter Problem

Free chlorine Analyzer Principle

Free chlorine Analyzer Principle

Learn More

D’Arsonval Movement

D’Arsonval Movement

Programmable Logic Controller (PLC) Questions and Answers

Programmable Logic Controller (PLC) Questions and Answers – 2

Float & Dial Level Gauge Principle

Float & Dial Level Gauge Principle

How to Calculate Network Speed?

Factors to Consider When Calculating Network Speed

Downloading Free PLC software

Step by Step Guidelines for Downloading Free PLC software

Asynchronous Motor Animation

Asynchronous Motor Animation

PLC analog output card

PLC Analog I/O and Network I/O

Car Parking System using PLC Programming

Car Parking System using PLC Programming

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?