Reading: How is Pressure Drop Calculated through a Valve ?
Inst Tools > Blog > Control Valves > How is Pressure Drop Calculated through a Valve ?
Last updated: April 20, 2019 1:36 pm
Control Valves Formulas
2 Comments
2 Min Read
The pressure drop across a valve is related to the flow rate passing through it, i.e. the greater the flow rate the higher the pressure drop and the lower the flow rate the lower the pressure drop.
Δp = (36Q/Kv)2Example of valve Pressure Drop :
Manufacturers publish a Flow Coefficient value to allow the calculation of pressure drop based on flow rate.
For metric units, i.e. m3/hour and bar or l/s and kPa, the flow coefficient is Kv, whereas, for imperial units, i.e. gpm and PSI, it is Cv.
As l/s and kPa are most commonly used, we will concentrate on Kv and not Cv.
The formula for calculating pressure drop is:
Δp = (36Q/Kv)2
Where:
Δp = pressure drop (kPa)
Q = flow rate (l/s)
Kv = flow coefficient (no units)
A flow rate of 0.225l/s passes through a D921 ¾” DRV (Double regulating Valve), calculate the pressure drop when the valve is fully open (FO).
Look up Kv value for ¾” D921 (Fully Open)
(Check Manufacturers published Flow Coefficient value in Datasheet)
Kv = 3.61
Δp = (36 x Q / Kv)2
Δp = (36 x 0.225 /3.61)2
Δp = 2.2442
Δp = 5.035 kPa
Also Read: Valves Questions & Answers
Types of Control Valve Trim
What is Flapper Nozzle System ?
Formula for Process Variable to Percentage Conversion
Electro Pneumatic Valve Positioner Schematic & Principle
Control Valve Air Lock Relay Working Principle
2 Comments
  • Junaid says:
    September 26, 2018 at 11:44 pm
    Excellent
  • ana says:
    March 13, 2023 at 7:56 pm
    Hi I have a question. I see that the lower the size of the valve the greater the pressure drop at a lower flow rate. Is there a reason behind this? Is it better to have a lower or higher-pressure drop?
Example of 3-15 psi to 4-20mA Conversion
Safety Relief Valve Quiz: Test Your Knowledge
Basics of Control Valve Sizing
Open and Closed Tank Level Calculations
Classification of Control Valves
Control Valve Volume Booster Working Principle
What is Cage-guided Globe Valve ?
What is an Air Valve? Purpose, Types, Advantages, Disadvantages
cut-away control valve
How Globe Valves Work ?
How to Do Maintenance of Control Valve Which is Stuck in Field?
Safety Valve
Compare Relief Valve and Safety Valve
Control Valve Tips and Tricks
Types of Pneumatic Valves
Types of Pneumatic Valves : Poppet & Spool
PCV
Difference between PCV and PRV
Control Valve in Last Position
Control Valve Fail Safe Action
Level Calculation with Remote Seals
Measurement and Instrumentation Objective Questions – Part 2
Sulphur Di-oxide Monitoring Questions & Answers
Center Tap Full-Wave Rectifier
Full-Wave Rectifier Circuit
PIN Diode Working Principle
buoyancy level transmitter
Displacer Level Transmitter Question & Answer
Perfume filling system PLC program
CX Programmer Example: Perfume Mixing and Filling System
What is Temperature
What is Temperature ?
Gas Chromatography Questions & Answers