Smart DP Transmitter Flow Meter Calculations
A Smart DP transmitter with built-in square root characterization is used to measure flow through a pipe.
The orifice plate range is 0 to 125 inches WC at 0 to 277 gallons per minute:
Smart DP transmitter Formula
A technician removes the transmitter from service and tests it by applying several air pressures to the “H” port while leaving the “L” port vented. Here are the As-Found results:
Smart DP transmitter Readings
Calculate the largest error, in percent of (output signal) span.
Also, determine whether this looks like a zero or span error, and whether that error exists in the input (ADC) of the smart transmitter or in the output (DAC).
Answer :
This is a span error in the output (DAC) of the smart transmitter, the greatest error being at the 100% point (20.100 mA instead of 20.000 mA = +0.625%).
More DP Transmitter Questions